Quote:
Originally Posted by kkdelhi I have a Microtek Heritage+ 600 UPS. Whenever the electricity goes off, the generator kicks in after about 30 seconds or so. But the UPS goes into the red and continues to give beep sound. Isn't the UPS supposed to go back to the normal mode when the generator kicks in? After all, it should treat power as it is - whether it comes through the mains or the generator.
What's wrong with it? I am technically  so please help. |
I am presuming this is is new UPS and does not work with the generator. No, all UPSs don't treat power as power - it treats them differently, so for it to work, your UPS has to be generator compatible. I think this Microtek model is not. I would suggest you change it for a Frontech model that is. There is also a PowerCom model that is generator compatible, but I would suggest you avoid it. I have lost 10 of those UPS (burnt) when on the generator line. The Frontech one works fine.