Old 24th June 2013, 11:53   #721
Gansan's Avatar
Thanked: 860 Times
Default Re: Inverter Batteries
The exide tubular battery supplied with my inverter becomes quite warm and consumes a litre of distilled water every week. No.1,5 and 6 cells seem to take in the most water. There seems to be no problem with the back-up though. Battery is 18 months old, original warranty 36 months.
What should be done? Shall I invoke warranty? I am not sure if it is a replacement warranty, at least not for the full three years.
Old 24th June 2013, 12:23   #722
drsingh's Avatar
Thanked: 446 Times
Thanks for the excellent links.
My next question is - Do modern inverters like the 850sine APC inverter have the circuitry to apply the equilization charge periodically?
Can i modify my existing generic automatic battery charger to output 14.4 volts?
drsingh is online now   Reply With Quote
Old 24th June 2013, 12:23   #723
Thanked: 979 Times
Points more to overcharging. Get the charging current checked.
In any case get the battery checked.
Old 24th June 2013, 12:53   #724
Thanked: 82 Times
Check the float voltage and see if its more then the battery manufactures rated specs.
aim120 is offline   Reply With Quote
Old 6th July 2013, 18:09   #725
Guite's Avatar
Thanked: 171 Times
Continuing from my earlier posts wrt to APC 850SINE paired with 2x100Ah batteries in parallel:
Problems reported:
1. Could not sustain plasma TV load.
2. Fluctuating voltage reading at TV plug.
3. Heating of cable.
Actions taken:
- called APC technician. He advised reducing cable length. Note that batteries are in the balcony to ventilate acid fumes
- reduced cable length from 2m+ to about 1.5m and reduced intermediate joint from two to one
- increased cable size from 6sqmm to 12sqmm each
- replaced one battery terminal (+) because it has 'rusted' (I don't know the correct term for it)
Results:
1. TV does not shut off by itself anymore when on inverter power. If PC is on, it cannot start from off state, otherwise it can power up from inverter.
2. No more fluctuating voltage reading. Ceiling fan speed also does not reduce drastically anymore when switching from mains power to inverter. BTW, mains is 255V and inverter output is 230V.
3. Cable heating up still occurs but hopefully not as bad as before. I have tried to make the intermediate joint as tight as possible.
I hope my experience is useful to someone.
Guite is offline   Reply With Quote
Old 7th July 2013, 05:55   #726
Is Prestolite inverter batteries are available in in the marker?
satran is offline   Reply With Quote
Old 7th July 2013, 14:57   #727
Thanked: 979 Times
Problems reported:
Actions taken:
Results:
All this points to undersized cables and may be faulty joints. Check the voltage drop across the cables when on full load. If it is more than 2% = 0.3V then you need to upsize the cables.
At 800VA the current drawn is at least 800/12=67A, more like 80A-90A if you factor the efficiency factor. The following gives capacities of wire needed. For 70A and 2% drop you require 22mm.sq and for 85A 27mm.sq.
http://www.calculator.net/voltage-dr...es=1&x=71&y=12
The less the voltage drop across the cables, the more efficient the battery utilization. For starting the vehicle undersize does not matter much as it is for a few seconds (though even there a thicker cable helps when battery is on its last legs), but for sustained usage loss of power in a cable is at the cost of the output from the inverter.
Old 7th July 2013, 22:17   #728
lurker's Avatar
Thanked: 577 Times
It's very bad idea to run plasma on 850VA sine wave APC. Go for 1400 VA 24V sine wave at minimum. You can connect the two batteries in series which would be perfect and pick up the plasma load easily. Go for Numeric or SuKam fusion series. Don't be so paranoid about service, these two are good on that front, at certain remote locations even better than APC who basically serve only in main centres nowadays and outsource service in secondary towns.
lurker is offline   Reply With Quote
Old 22nd July 2013, 12:30   #729
Hi All,
I have one APC UPS (800 VA) installed at my home 4 years back. Since last one month onwards, I have observed that the batteries are getting heated when it recharge mode.
What is the reason behind the batteries getting overheated.
Appreciate your help.
Old 22nd July 2013, 13:32   #730
Thanked: 82 Times
Originally Posted by satran View Post
Hi All,
Overcharging,check the float voltage.
4 years is a long time for a SMF battery,I believe its EOL and needs replacing.
Old 22nd July 2013, 14:28   #731
How to check the float voltage, I don't have any idea about batteries. I think the battery is semi tubular one, because I used to fill the Distil water 3 months once.
Old 22nd July 2013, 16:25   #732
Thanked: 82 Times
Use a multimeter to check the voltage.
If its a semi tubular one did you check whether the water is low,the battery warms up typically because of a higher charge voltage.
Old 22nd July 2013, 20:34   #733
Thanked: 92 Times
The trusty Exide invaQueen 450 battery of my inverter was replaced by an Exide InvaRED 450+ yesterday after reliable service of 7 odd years. The old one was barely providing power backup.The cost of the new battery was 8K after deducting buyback price of the old battery.
JustCause is offline   Reply With Quote
Old 23rd July 2013, 09:30   #734
Battery volt is showing 12.25 v
Old 23rd July 2013, 11:23   #735
Thanked: 979 Times
Is this under load or without.
Normally fully charged batteries should show 2.2V/cell =13.2V, so 12.25 is a bit low if it is without load.
Inverter or generator? mrhap Gadgets, Computers & Software 728 12th August 2017 02:46
Car Battery to 220V AC convertor / inverter for charging laptop etc sreeku In-Car Entertainment 163 25th September 2016 23:00
Myth: UPS can't run on inverter? linuxtechie Gadgets, Computers & Software 17 24th October 2008 15:47