Old 8th July 2013, 11:10   #3226
Senior - BHPian
 
Join Date: Aug 2010
Location: Delhi
Posts: 2,614
Thanked: 3,024 Times
re: The home / office air-conditioner thread

The 2 ton AC will be drawing around 10A current while running and at least 30A when starting, so 6A is just not right. (9.8 as per literature)
http://www.voltasac.com/index.php?op...4&cid=7&vr=164

With modern cables 2.5 sq.mm is the border line for 2 ton AC, 4 is preferred. The thinner the conductor the hotter it will get, which in hot ambient temparature will lead to insulation melting resulting in shor circuit and fire. So it is better to err on the thicker side and install 4 sq.mm.

http://www.qflexcable.com/flexible.htm
Aroy is offline  
Old 8th July 2013, 11:27   #3227
BHPian
 
Join Date: Apr 2010
Location: Cochin
Posts: 209
Thanked: 213 Times
re: The home / office air-conditioner thread

Quote:
Originally Posted by diyguy View Post
I would take this very seriously. I am not an expert but my DB phase changer caught fire when we had our hall 2T and my bedroom 1.5t running at the same time. I now have a smoke detector sitting inside my DB and I do not switch on these two acs in parallel.
Thank you for the warning diyguy. 4 sq mm it will be!

Quote:
Originally Posted by Thad E Ginathom View Post
I don't know about calculations, but in my motherland, 1.5-sq-mm cable is used for lighting circuits. I suggest that you accept your technician's advice. Always safer to over-specify with cable, plugs and sockets.

Remember that devices like ACs have a much heavier start-up load.
This is the same information(1.5 sqmm = light/fan circuit) conveyed to me by the AC technician. Going with the over spec wiring.

Quote:
Originally Posted by Aroy View Post
The 2 ton AC will be drawing around 10A current while running and at least 30A when starting, so 6A is just not right. (9.8 as per literature)
http://www.voltasac.com/index.php?op...4&cid=7&vr=164

With modern cables 2.5 sq.mm is the border line for 2 ton AC, 4 is preferred. The thinner the conductor the hotter it will get, which in hot ambient temparature will lead to insulation melting resulting in shor circuit and fire. So it is better to err on the thicker side and install 4 sq.mm.

http://www.qflexcable.com/flexible.htm
4 sqmm it will be! BTW, This is a 1TR AC - and it is 6A per Bluestar. But wont be taking risks - Will go for higher spec wiring.

Thank you all for your precious advice.
Sedate is offline  
Old 10th July 2013, 08:38   #3228
BHPian
 
johy's Avatar
 
Join Date: Mar 2006
Location: Siliguri
Posts: 992
Thanked: 634 Times
re: The home / office air-conditioner thread

Guys,I have a completely newbie question related to split ACs, do the pipes have to filled with gas during installation?

I have installed a few ACs in my new house (still not completed), so have not tested out the ACs yet. Please advise.
johy is offline  
Old 10th July 2013, 09:45   #3229
Senior - BHPian
 
sgiitk's Avatar
 
Join Date: Dec 2007
Location: Gurugram
Posts: 7,971
Thanked: 4,809 Times
re: The home / office air-conditioner thread

@johy; Yes, the pipes need to be evacuated and then filled. This is along with the cooling coils. Normally the compressor unit is shipped with the refrigerant and once the valves are opened then everything goes, assuming there are no leaks.
sgiitk is offline  
Old 27th July 2013, 12:30   #3230
BHPian
 
coolbareilly's Avatar
 
Join Date: Oct 2007
Location: Delhi
Posts: 194
Thanked: 16 Times
re: The home / office air-conditioner thread

Hi Friends, I need a small help.
I purchased Hitachi Summer QC 1.5 ton AC in June 2011. Since I purchased AC in the very first year of purchase it developed a problem with the front display panel and it took almost 3-4 weeks to get it replaced. And yesterday AC suddenly stopped working and displaying error code E9. After researching a lot on internet, I found that the error code is somehow associated with DC Fan moter. And as per different forums on internet it seems to be pretty expensive (Rs7000 approx). I am very disappointed with the product. I have 4 other ACs from Whirlpool, Carrier, Voltas but they have never developed any of the issue in the span of last more than 8 years.
Can anyone of you have email IDs of customer support head, Sales Head or escalation matrix, then it would be very helpful. Even after spending 30K for AC I am not getting peace of mind.

Thank you all in advance.
coolbareilly is offline  
Old 27th July 2013, 15:10   #3231
BHPian
 
Join Date: Sep 2012
Location: Baroda
Posts: 208
Thanked: 131 Times
re: The home / office air-conditioner thread

Question for fellow members:

I have 4 Daikin A/cs installed and have called for their AMC quotes. The charge is Rs.2200/- per AC which includes 4 visits i.e. one every quarter. The visit will include dry services and will be routine.

What I want to know is Rs. 525/- per visit reasonable and/or what should be a reasonable amc charge for these A/cs. All inputs will be helpful in finalizing the price and giving the AMC.
abs182 is online now  
Old 27th July 2013, 15:34   #3232
BHPian
 
diyguy's Avatar
 
Join Date: Jun 2009
Location: Chennai
Posts: 521
Thanked: 588 Times

Quote:
Originally Posted by abs182 View Post
Question for fellow members:

I have 4 Daikin A/cs installed and have called for their AMC quotes. The charge is Rs.2200/- per AC which includes 4 visits i.e. one every quarter. The visit will include dry services and will be routine.

What I want to know is Rs. 525/- per visit reasonable and/or what should be a reasonable amc charge for these A/cs. All inputs will be helpful in finalizing the price and giving the AMC.
Sounds about right. If it covers parts replacement, it is cheap.
I have 4 acs but none under Amc. I find that once the dealer takes Amc it's a pain to get them to visit per our convenience. So I nowadays pay as I call them or just clean them myself...
diyguy is offline  
Old 27th July 2013, 16:24   #3233
BHPian
 
Join Date: Sep 2012
Location: Baroda
Posts: 208
Thanked: 131 Times
re: The home / office air-conditioner thread

Quote:
Originally Posted by diyguy View Post
Sounds about right. If it covers parts replacement, it is cheap.
I have 4 acs but none under Amc. I find that once the dealer takes Amc it's a pain to get them to visit per our convenience. So I nowadays pay as I call them or just clean them myself...
I think doesn't include parts replacements. It covers 10 or so service checks that they carry out which included complete cleaning of the machines etc apart from the filter. My query is that are 4 services necessary and also 2 A/cs aren't used as frequently as the other 2 which are in the bedrooms. Please advise. And if I call them on adhoc basis what should be the frequency of their visits?
abs182 is online now  
Old 27th July 2013, 18:40   #3234
BHPian
 
diyguy's Avatar
 
Join Date: Jun 2009
Location: Chennai
Posts: 521
Thanked: 588 Times
re: The home / office air-conditioner thread

Quote:
Originally Posted by abs182 View Post
I think doesn't include parts replacements. It covers 10 or so service checks that they carry out which included complete cleaning of the machines etc apart from the filter. My query is that are 4 services necessary and also 2 A/cs aren't used as frequently as the other 2 which are in the bedrooms. Please advise. And if I call them on adhoc basis what should be the frequency of their visits?
If it is not parts, I wouldnt go with all 4 with the same dealer. What happens is they try to service 2-3 a/c on the same visit and they end up doing a shoddy job on the 2nd and 3rd as they get tired and also we lose a whole day sitting with them. Best to call them adhoc whenever you want. I think instead of 525, they may charge you 600-650 per visit, but I think that is best.
diyguy is offline  
Old 28th July 2013, 10:44   #3235
Senior - BHPian
 
Join Date: Aug 2010
Location: Delhi
Posts: 2,614
Thanked: 3,024 Times
re: The home / office air-conditioner thread

Even I think that as you have 4 AC there is no need for AMC. I get my AC cleaned once a year, except the window type in my bedroom which collects a lot of dust on the outer coil, hence twice for it.

If the AMC were with parts it would be justified, but paying 10k each year is just not worth it - you get a free AC every third year. So I suggest that you negotiate the total service cost, call them once a year, and ensure that if there is only one set of service personell they service only 2 AC per day.
Aroy is offline  
Old 29th July 2013, 18:46   #3236
BHPian
 
Join Date: Oct 2009
Location: Chandigarh
Posts: 55
Thanked: 125 Times
re: The home / office air-conditioner thread

Hello all,

Delayed update but had gone ahead and purchased Hitachi 1.5 Ton Summer TM Model in June (sorry could not update the thread earlier). The AC is very nice and while the room is large, it does cool down the room quite effectively. Looks nice as well :-). So, for now, me and family are satisfied Hitachi customers. Purchased a V-Guard stabilizer as well (though had I been more regular with my visits to the forum, might have gone for maybe a Sollatek AC Guard instead). What is done is done for now though :-)

Anyone looking for details about the AC - http://www.hitachi-hli.com/productdetail/Summer-TM/

Thanks to sgiitk, bluevolt, khoj, anupmathur, akshay1234 for replying and providing inputs.

Quote:
Originally Posted by sukhoi View Post
Hello,

Am in the market for a window AC and looking for suggestions / inputs. Have never owned one before so absolutely clueless :-)

Cheers
Quote:
Originally Posted by bluevolt View Post
Panasonic 1.5 ton cube will be real value for money.
Quote:
Originally Posted by khoj View Post
sukhoi, on one hand you say that you have not owned an airconditioner before and the you go on to comment on the quality of machines from the brand General. ... Do elaborate .. It will help in updating information here vis a vis the current market dynamics.
Quote:
Originally Posted by anupmathur View Post
I would say a 1.5 ton would do fine. You might need to be patient for things to cool down.
If it is a living room, you should be looking at a 2 ton unit.
Quote:
Originally Posted by akshay1234 View Post
Get a 2 ton. The room size is large and while a 1.5 ton may be just enough, it will take longer to cool than a 2 ton.
Quote:
Originally Posted by sgiitk View Post
I tend to agree, but then there are two reasons you may not. While 1.5TR is a commodity item, a 2TR is not. Also you will find the COP lower for the 2TR.
sukhoi is offline  
Old 30th July 2013, 08:54   #3237
Senior - BHPian
 
sgiitk's Avatar
 
Join Date: Dec 2007
Location: Gurugram
Posts: 7,971
Thanked: 4,809 Times
re: The home / office air-conditioner thread

@sukhoi; Window ACs do not normally need serious attention for ten plus years, so you should be Ok.
sgiitk is offline  
Old 31st July 2013, 17:43   #3238
BHPian
 
EFF-EIGHT-BEE's Avatar
 
Join Date: Jan 2010
Location: Patiala
Posts: 196
Thanked: 113 Times
re: The home / office air-conditioner thread

Hello mates, I am posting this query on behalf of my sister. She is looking for 1.5T ac preferably window ac as she has recently joined civil services which involves transfers after some time so split won't be practical for her. She has set a budget of 30k(slightly moveable). We did checked some ac online but found that choices are not that great as compared to splits which is increasing the confusion part so please help us out.
EDIT- a tough machine is preferred which can bear frequent transportation.

Last edited by EFF-EIGHT-BEE : 31st July 2013 at 17:51. Reason: Additions.
EFF-EIGHT-BEE is offline  
Old 1st August 2013, 11:56   #3239
Senior - BHPian
 
Join Date: Aug 2010
Location: Delhi
Posts: 2,614
Thanked: 3,024 Times
re: The home / office air-conditioner thread

Quote:
Originally Posted by EFF-EIGHT-BEE View Post
Hello mates, I am posting this query on behalf of my sister. She is looking for 1.5T ac preferably window ac as she has recently joined civil services which involves transfers after some time so split won't be practical for her. She has set a budget of 30k(slightly moveable). We did checked some ac online but found that choices are not that great as compared to splits which is increasing the confusion part so please help us out.
EDIT- a tough machine is preferred which can bear frequent transportation.
Best bet is to find what brands are patronised by the Government. The service for these will be available where ever your sister is transferred.

Most of the window AC are quite tough and can be easily transported, provided
. You keep the original shipping carton, or else have a good wooden box specifically made to transport the AC
. You keep the restraining bolts for the compressor, which are taken off during installation, and use them while transporting. The same applies to most of the WM.

I remember that most of my friends who were in transferable jobs (Armed forces, Banks, Civil Service etc), had a boxes made for most of their appliances. They also had boxes for transporting crockery, cutlery and all the other delicate stuff. For the rest there were steel trunks which can withstand rough handling. At regular intervals, when they were transferred, they would pack every thing into custom made boxes, transport, unpack and store the boxes.

Last edited by Aroy : 1st August 2013 at 11:58.
Aroy is offline  
Old 1st August 2013, 12:03   #3240
BHPian
 
EFF-EIGHT-BEE's Avatar
 
Join Date: Jan 2010
Location: Patiala
Posts: 196
Thanked: 113 Times
re: The home / office air-conditioner thread

Quote:
Originally Posted by Aroy View Post
Best bet is to find what brands are patronised by the Government.
Thankyou very much for your useful extra inputs, can you please elaborate a bit on the patronised part?
EFF-EIGHT-BEE is offline  