Solar Plant Setup on my Rooftop - Off-grid (for now) - 3 KVA Start Date - 18-06-2024 ; Finish Date - 08-08-2024 (about 45 days)
These posts details how you can setup your own solar plant yourself with just a little technical understanding of the basics. I was quoted minimum of 2.5Lacs (for the specifications of materials that I have used) and I have saved nearly 1 lac by doing it myself as the total cost of the plant was in the vicinity of Rs.1.5 Lacs.
This is the story of me converting my
'dilapidated' rooftop into a
lifelong solar plant. I took my own sweet time, at my own sweet pace, but completed it at my convenience.
So my city, Meerut, is situated at a latitude of 28.984. For any Solar Plant in our region, we require it to be
SOUTH Facing and tilted at the approximate latitude of your area i.e.
25~30 degrees in my case, so that it gets maximum solar energy throughout the year. This is the
1st principle.
So this was was dilapidated rooftop, which was 30+ years old. Luckily I had some strong basic steel structure already installed, as it was previously supporting a cement roofing sheets structure. Luckily it was
South Facing and at a 30 degrees angle. Exactly what I needed. So I decided to remove all the old sheets, and put up the Solar Plant here.
This is how it looks
NOW completed, with 3450 watts capable
6 Solar Panels -
And this is my off-grid
Solar PCU of 3000VA (2400 Watts) with 2x12V 200Ah Exide Solar Batteries with FULL 5 years warranty.
I was currently running my house on a very old 1500VA Microtek Inveter and that was sufficient for the Light load. But with the Solar System I also wanted to add all my Non-AC power load including 2 x 400L Refrigerators. So the first thing was to figure out my normal running total house load without the AC's.
As is evident in this picture of the mains Ampere/Volt meters, that I have attached after our electric supply meter, the normal light load is about 650~700 watts and the maximum power load including 2 refrigerators etc. is about 850 watts, excluding the Air Conditioners. So the minimum total solar system needed to be capable of outputting
1550 watts.
So I started researching what all would be needed from my end to convert my existing MS structure into a structure capable of fixing the solar panels without issues. The main thing I came to find out, that is needed, is this Galvanised Iron U channel known as
Perlin in their terminology, on which the solar panels can easily be tightened by
Z Clamps and
U clamps made of aluminium. This is how a Perlin is supposed to look like -
So the task starts, to convert this Cement Sheet structure into Solar Panel capable structure. I calculated that the total structure that I had was easily capable of taking 20 x Solar Panels. I needed to start off with just
6 and maybe add on
8~10 panels later as a
On-Grid System. The basic structure, earthing etc. will all be shared.
Some initial calculations -
A rough design was made -
Culminating into a more legible
Perlin Design for 8 panels (2 in reserve)
This is how 1 feet of Perlin looks in
cross section. It should be minimum 2 to 3 mm in thickness -
And these were the U and Z clamps needed. All available also on Amazon.
I searched out local vendors for these items and luckily one of them agreed to supply me the required lengths of Perlin plus other important items like the DC specific Wire, a DC side Distribution Box (called DCDB in their terminology), clamps, MC4 connectors etc. -
A closeup of the
DCDB box (more on this later) -
All these items costed me 19000 Rs. -
With full GST Bill -
Basic innards of this
3 into 1 (that I needed as per my plan, which you will see later)
DCDB Box (cost about 2k). It basically contains DC Fuses and a DC Surge Protection Device with some connectors BUT was missing a DC MCB, which I was not comfortable with -
A closer look at the DC fuses -
Now a closer look into
understanding the GI Perlin and how the Clamps are attached -
Side view -
Some dimensions -
And the Bolt/s with which it will attached to my existing MS structure at various points to make it last for the next 30 years -
A cross-sectional view. Notice the spring loaded bolts -
With added
spring washers, to withstand the harshest of weather conditions -
I had to change the attachment bolts to these new SS ones from the GI ones of the required increased length for more durability and longevity -
Notice the Spring Washer that I added -
Some
2 into 1 and
3 into 1 MC4 connectors that I bought from Amazon, but never needed -
30 photos limit reached.
Continued...