Re: The home / office air-conditioner thread

Quote:
Originally Posted by NPV View Post
Noob electricals question.
Our Daikin split AC stopped working earlier this week and the diagnosis is that main boards of both indoor and outdoor units have gone bust. We had a power surge few days ago but the AC wasn't being operated at the time though the wall socket's switch was ON. Connection is from wall socket to V-Guard stabilizer to AC indoor unit. Wondering why the stabilizer didn't cut off output to the AC during the surge ? What could be a possible solution to avoid this in future ? (The circuit also has a MCB)
Stabilizer needs some time to react to the surge. The surge would have done the damage by the time the stabilizer could react. You need a spike buster before the stabilizer since the spike buster will cut off the supply first in case of a surge.
sagarpadaki is offline  
Old 1st March 2019, 15:06   #6107
Distinguished - BHPian
 
Thad E Ginathom's Avatar
 
Join Date: Jun 2007
Location: Chennai
Posts: 11,005
Thanked: 26,447 Times
Re: The home / office air-conditioner thread

Quote:
Originally Posted by sagarpadaki View Post
Stabilizer needs some time to react to the surge. ...
And the same thing applies to the MCB.

Sorry to hear of your loss. Power surges can be expensive.
Thad E Ginathom is offline  
Old 1st March 2019, 17:19   #6108
Team-BHP Support
 
Chetan_Rao's Avatar
 
Join Date: Jul 2010
Location: Bangalore
Posts: 5,908
Thanked: 24,115 Times
Re: The home / office air-conditioner thread

Quote:
Originally Posted by NPV View Post
....Wondering why the stabilizer didn't cut off output to the AC during the surge ? What could be a possible solution to avoid this in future ? (The circuit also has a MCB)
Commercially available stabilizers are electromechanical in nature (that's why you hear the relays clicking when they're in action) with a reaction time in milliseconds (thousandths of a second). The best ones you can find will still have reaction times around 10 ms.

Power spikes/surges occur in an entirely different and far smaller timeframe (nanoseconds, that's a billionth of a second), so your stabilizer is useless against a power spike/surge, it's not designed for it.

You need a spike/surge protector before the stabilizer on the A/C input.

Last edited by Chetan_Rao : 1st March 2019 at 17:23.
Chetan_Rao is offline  
Old 1st March 2019, 20:37   #6109
NPV
Distinguished - BHPian
 
NPV's Avatar
 
Join Date: Oct 2009
Location: Namma Bengaluru
Posts: 7,220
Thanked: 10,265 Times
Re: The home / office air-conditioner thread

Quote:
Originally Posted by Chetan_Rao View Post
You need a spike/surge protector before the stabilizer on the A/C input.
Any examples of such products ?
Will the regular multi socket extension cord (power strip) with surge protection via a fuse do the job ?
NPV is offline  
Old 2nd March 2019, 12:25   #6110
BHPian
 
Prowler's Avatar
 
Join Date: Jul 2008
Location: Madras
Posts: 775
Thanked: 1,329 Times
Re: The home / office air-conditioner thread

Quote:
Originally Posted by NPV View Post
Any examples of such products ?
Will the regular multi socket extension cord (power strip) with surge protection via a fuse do the job ?
I have mentioned about this earlier here. Electronic gadgets don't take kindly to transients and surges. Your stabilizer will not protect your precious gadgets from such transients.

What you need is a Surge Buster which uses a MOV (metal oxide varistor). When it comes to high current consuming Airconditioners, Washing machines and other equipment, do NOT use ordinary extension cords. You need something that can carry at least 20 A safely.

So what this means is you need to buy a 4pole Surge Protection Device (for 3 phase supply) which can be fitted in your mains input box. These devices have typical response time of 25 nS. And they can 'sink' 20000 A.

They will protect your electrical gadgets from even lightening strikes in the supply line.

We used to suffer electronics causalities regularly every monsoon in Madras until we rigged these devices in our mains line. Not just that, we even took the trouble of fitting a MOV 275 V/20A device for every socket with a MCB so that even locally induced transients and surges can be arrested before they do any serious damage.

Last edited by khan_sultan : 13th April 2019 at 08:06. Reason: line spacing for better readability
Prowler is offline   (3) Thanks
Old 2nd March 2019, 12:35   #6111
BHPian
 
diyguy's Avatar
 
Join Date: Jun 2009
Location: Chennai
Posts: 517
Thanked: 578 Times

Quote:
Originally Posted by Prowler View Post
So what this means is you need to buy a 4pole Surge Protection Device (for 3 phase supply) which can be fitted in your mains input box. These devices have typical response time of 25 nS. And they can 'sink' 20000 A.
Do you mean something like this?
https://www.amazon.in/dp/B01N78G0JE/..._dNIECb2SR02P0
diyguy is offline  
Old 2nd March 2019, 12:48   #6112
BHPian
 
Prowler's Avatar
 
Join Date: Jul 2008
Location: Madras
Posts: 775
Thanked: 1,329 Times
Re: The home / office air-conditioner thread

Quote:
Originally Posted by diyguy View Post
Yes. But there are other companies like Schneider too. Whilst at it make sure that you have a proper earth/ground. These devices need a low impedance/resistance ground for proper operation.
Prowler is offline  
Old 3rd March 2019, 18:16   #6113
NPV
Distinguished - BHPian
 
NPV's Avatar
 
Join Date: Oct 2009
Location: Namma Bengaluru
Posts: 7,220
Thanked: 10,265 Times
Re: The home / office air-conditioner thread

Quote:
Originally Posted by Prowler View Post
But there are other companies like Schneider too. Whilst at it make sure that you have a proper earth/ground. These devices need a low impedance/resistance ground for proper operation.
Thanks. Can you please share details of the specific products (Schneider MOV) that you have used both at main input (is it at the cut-out in the street pole from your connection is tapped or is the device fixed at the main meter ?) And also the MOV outlets to which the appliance/electronic device is connected ?
We have a single phase electric connection, not 3 phase, not sure if the MOV products to be used will be different for our usage compared to what you have used for the 3 phase connection.

Last edited by NPV : 3rd March 2019 at 18:18.
NPV is offline  
Old 4th March 2019, 09:46   #6114
BHPian
 
Prowler's Avatar
 
Join Date: Jul 2008
Location: Madras
Posts: 775
Thanked: 1,329 Times
Re: The home / office air-conditioner thread

Quote:
Originally Posted by NPV View Post
Thanks. Can you please share details of the specific products (Schneider MOV) that you have used both at main input (is it at the cut-out in the street pole from your connection is tapped or is the device fixed at the main meter ?) And also the MOV outlets to which the appliance/electronic device is connected ?
We have a single phase electric connection, not 3 phase, not sure if the MOV products to be used will be different for our usage compared to what you have used for the 3 phase connection.
That is odd. Normally most of the Indian Electricity Boards will provide a maximum of 15 A per phase supply to a house. If you have a single phase supply, the maximum current you can draw is 15 A - limited by your meter. Any overload - above 150% will damage the electronic type meter. The old fashioned cog wheel meter may withstand more short term overload.

A 15 A supply will restrict the load you can use in your house. Please check again your utility Supply line. You should find something like this:
20 A/30 A fuse box per phase feeding your meter. After the meter, it will go towards a switch box and then to small circuit breakers feeding individual lines.

You can buy any good SPD (like this eg: Havel's : https://www.havells.com/en/consumer/...evice-(7).html)
Connect this Surge Protection Device (SPD) after the MCB at the entry point of mains supply. If there is any surge, the SPD will trigger the source to the ground. It is very rare for the device to fail. It can be replaced as a cartridge.

Go to your friendly neighborhood electronics component store and buy one or more of MOV 275/20 . They don't cost much. Ask your electrician to fix this component after the MCB inside your metal socket of your Airconditioner.

Last edited by khan_sultan : 13th April 2019 at 08:06. Reason: line spacing for better readability
Prowler is offline   (1) Thanks
Old 5th March 2019, 00:04   #6115
BHPian
 
diyguy's Avatar
 
Join Date: Jun 2009
Location: Chennai
Posts: 517
Thanked: 578 Times

Quote:
Originally Posted by Aroy View Post
. I bought an LG 5 star dual inverter AC; which had an MRP of 59,000/ + 1,500 for installation; through PAYTM. After all the cashback (PAYTM and ICICI), my cost was around 34K.
Sounds like a great deal. Kindly share the model number if you have it handy. I suppose these deals will now be available post the summer.
diyguy is offline  
Old 5th March 2019, 09:31   #6116
Senior - BHPian
 
Join Date: Aug 2010
Location: Delhi
Posts: 2,582
Thanked: 2,741 Times
Re: The home / office air-conditioner thread

Quote:
Originally Posted by diyguy View Post
Sounds like a great deal. Kindly share the model number if you have it handy. I suppose these deals will now be available post the summer.
LG-Q18HUZD

The deals change throughout the year, so you have to be on the lookout. I bought my AC in beginning of June, which is middle of harsh summer.

It all depends on the market, and if the appliances are not selling then you will start getting deals, which will keep getting sweeter and sweeter if the sales are dull.

Here is the least expensive model now
https://paytmmall.com/lg-1-5-ton-5-s...hild_site_id=6

But
. Cashback is low (5% vs 13%)
. Installation is not free (added cost of 1,500)
. No cashback from banks (was 2,500 from ICICI and HDFC)

I guess as the summer approaches, the deals will get better
Aroy is offline  
Old 11th March 2019, 10:28   #6117
BHPian
 
diyguy's Avatar
 
Join Date: Jun 2009
Location: Chennai
Posts: 517
Thanked: 578 Times

Need some help with the right procedure to check refrigerant level in a R22 Daikin 1.5T split ac. I called Daikin and they sent a contracted dealer home. I insisted to the guy that my ac is cooling but low and need to ensure gas is topped up.

He did some indoor cleaning for about 5-8 mins and then the outdoor unit he poured water on the heat exchanger coils for about 5 mins. He used the pressure gauge and showed me 40 psi but didn't wait much for the pressure to rise while the compressor was on. He then connected a cylinder of R22 and did not turn it on or off. I was watching keenly, he was on a call and seemed to pretend he did something for a few seconds and told me he finished. He then connected the gauge and waited patiently for the pressure to rise to 60psi. This was unlike in the beginning when he showed me 40psi which he removed almost instantly. I told him I need to see atleast 80psi but he said he cannot add more.

I refused to pay him and told him will check overnight and then pay. The cooling has not improved significantly which one would expect with a full refrigerant level. I had paid him 1150 rs yesterday and have a balance of 500 that I do not intend paying and will ask Daikin to send me another team to measure and topup the gas if needed.

Please let me know if the process of gas checking that he did was correct or he was trying to cheat. Also he claimed that gas filling takes just 1-2 seconds which I totally did not buy. Was he right?

I know 80psi is high but he himself told me it should be at 80psi initially. One thing I noticed is that the power consumption from about 1750w has fallen to 1550w when the ac is running at 18° after the cleaning.

Last edited by khan_sultan : 13th April 2019 at 08:08. Reason: formatting for better readability
diyguy is offline  
Old 11th March 2019, 10:56   #6118
BHPian
 
kavensri's Avatar
 
Join Date: Oct 2015
Location: BengaLooru
Posts: 327
Thanked: 738 Times
Re: The home / office air-conditioner thread

I have one noob question.
I brought my Mitsubishi Electric AC in 2016. This will be my 4th year running. Previously I have used it for 3 months in a year, average of 4 hours per day.
My question is, do I need to get anything checked up, like gas level? I am not facing any issues with the cooling level, but just wanted to know whether I need to get any preventive service checkup to be done?
kavensri is offline  
Old 12th March 2019, 11:34   #6119
BHPian
 
Join Date: Feb 2019
Location: Noida
Posts: 80
Thanked: 195 Times

Need some expert inputs.

I am planning to buy a AC for my living room.

Floor: Top Floor (living room becomes heat chamber in summer)
Location: Noida
Area: ~220 sq ft

Estimated Running Time: 3-5 hours daily

My heart beats for Mithshubishi 2.2 Tonne Inverter AC. But at 70K, it is very expensive. Currently Carrier 2 Tonne 3 Star Inverter AC is available for Rs 42K on Flipkart. Panasonic 2 Tonne 5 Star AC is available for Rs 47K, while LG 2 Tonne 3 Star is selling at 49K.

The Panasonic window AC in my bedroom started giving problem after the first year. From PCB failure to gas leakage, it has been plagued with issues from the time the warranty got over. So I am not very keen on Panasonic.
Moreover, since the air in Nodia is very toxic and corrosive, people suggest that the condenser should be robust and have special coating.

Kindly advise which brand should I go for. How about brands like Midea or Whirpool? Are they good?

Quote:
Originally Posted by kavensri View Post
I have one noob question.
I brought my Mitsubishi Electric AC in 2016. This will be my 4th year running. Previously I have used it for 3 months in a year, average of 4 hours per day.
My question is, do I need to get anything checked up, like gas level? I am not facing any issues with the cooling level, but just wanted to know whether I need to get any preventive service checkup to be done?

I would advise not to tinker with the AC. Mitsubishi ACs are the best in the market and they have a very solid built. Just clean the filter with running water at the beginning of the season.

Moderator's Note: Do not make back to back posts. Use the Multiquote option to respond to multiple people at one go.

All the back to back posts have been merged.

Last edited by Samurai : 21st April 2019 at 12:30. Reason: non-standard img removed
MBond007 is online now  
Old 12th March 2019, 13:39   #6120
Senior - BHPian
 
Join Date: Aug 2010
Location: Delhi
Posts: 2,582
Thanked: 2,741 Times
Re: The home / office air-conditioner thread

Quote:
Originally Posted by MBond007 View Post
Need some expert inputs.

I am planning to buy a AC for my living room.

Floor: Top Floor (living room becomes heat chamber in summer)
Location: Noida
Area: ~220 sq ft

Estimated Running Time: 3-5 hours daily
....[/b]
I have excellent ownership with LG dual inverter AC. Their service is much better than Hitachi and Daikin (which I still have) and their extended warranty covers all but some rubber parts -
. 2 Service a year
. Gas
. Compressor
. Heat exchangers
. Electronics

So you are covered for 5 years at 16K or so.